How Can I Convert Analog Data Read from PLC to the Correct Temperature Value?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • DataStream
    Junior Member
    • 11.08.2025
    • 10

    #1

    How Can I Convert Analog Data Read from PLC to the Correct Temperature Value?

    I receive raw data from a PLC in the range of 0-4095. This data actually represents a temperature between 0-150°C. How can I convert this raw data to the correct temperature value in the SCADA software?
  • Technical Support
    Member
    • 11.08.2025
    • 40

    #2
    We have a feature that allows you to scale raw values to obtain the corresponding result values.

    By using the "Engineering Scale" property in the tags, you can specify the raw and desired value ranges to scale the tag values accordingly.


    Click image for larger version

Name:	engineering_values.png
Views:	7
Size:	25.1 KB
ID:	148
    Last edited by Technical Support; 14-08-2025, 11:58.