I'm connecting a new booster station to Omnivex SCADA over Modbus TCP. Pressure, flow and motor current come from holding registers and they read correctly.
The pump running and fault signals are digital. The panel builder's list says "Discrete Inputs 10001–10008". I created a second frame with Start Address 10001, Quantity 8 and the same Function Type as my analog frame, and the tags in that frame are always 0, even when the pump is clearly running. There is no error on the channel.
What am I doing wrong with the digital signals?
The pump running and fault signals are digital. The panel builder's list says "Discrete Inputs 10001–10008". I created a second frame with Start Address 10001, Quantity 8 and the same Function Type as my analog frame, and the tags in that frame are always 0, even when the pump is clearly running. There is no error on the channel.
What am I doing wrong with the digital signals?